harritr1
Member
- Location
- Houston, TX
I am a new engineer graduate and I have been given a project where I am sizing replacement cable for a feeder to an ATS. I have everything figured out (voltage drop, grounding etc.) except for ampacity and that's because there is about a 16 foot section of a 560 foot run that goes underground in PVC that is encased in concrete (the rest of the pull is all in uncovered cable tray). Section 310.15(B)(3)(3) in NFPA 70 2017 edition states that:
"(3) Adjustment factors shall not apply to undergroundconductors entering or leaving an outdoor trench if thoseconductors have physical protection in the form of rigid metalconduit, intermediate metal conduit, rigid polyvinyl chlorideconduit (PVC), or reinforced thermosetting resin conduit(RTRC) having a length not exceeding 3.05 m (10 ft), and ifthe number of conductors does not exceed four."
My interpretation of that paragraph is that I need to de-rate this cables ampacity but I cannot figure out with what factors to do it. Is this just a passage that is supposed to refer me to another table in the NEC or is it something that will involve just a little math like adjusting for ambient temperature? If you could be specific in your answers on where you reference the code it would be very helpful.
Thank you.
"(3) Adjustment factors shall not apply to undergroundconductors entering or leaving an outdoor trench if thoseconductors have physical protection in the form of rigid metalconduit, intermediate metal conduit, rigid polyvinyl chlorideconduit (PVC), or reinforced thermosetting resin conduit(RTRC) having a length not exceeding 3.05 m (10 ft), and ifthe number of conductors does not exceed four."
My interpretation of that paragraph is that I need to de-rate this cables ampacity but I cannot figure out with what factors to do it. Is this just a passage that is supposed to refer me to another table in the NEC or is it something that will involve just a little math like adjusting for ambient temperature? If you could be specific in your answers on where you reference the code it would be very helpful.
Thank you.