mbrooke
Batteries Included
- Location
- United States
- Occupation
- Technician
I am design evaluating an underground transmission system consisting of a 330kv loop. This loop will supply several bulk substations which in turn each will supply 110kv area substations. The load on each bulk substation is about 1000MVA max, and each area substation feeds about 180MVA of network load. Parts of the loop will carry approximately 3000MVA when all is said and done.
The question is, how many cables and of what size would you use? Fewer cables of higher ampacity or many cables of lower ampacity? I am thinking 6 circuits of 2 per phase 2000kcmil copper 362kv solid dielectric cables (grounded at both ends encased in concrete duct banks derated accordingly) from bulk substation to bulk substation and 4 145kv 1000kcmil solid dielectric cables between the bulk and each area substations.
Second- what contingency level should I design this for? I am currently thinking N-2 (2 circuits out) on both 330 and 110kv, as failures of underground cables take much more time to repair.
Third, though not really the scope of my question but still partly relevant- cable charging compensation shunt reactors should be placed on each cable bay or lumped and placed on the bus?
I have no reference to go by... I am open to any suggestions/critique. The substations will be GIS btw.
The question is, how many cables and of what size would you use? Fewer cables of higher ampacity or many cables of lower ampacity? I am thinking 6 circuits of 2 per phase 2000kcmil copper 362kv solid dielectric cables (grounded at both ends encased in concrete duct banks derated accordingly) from bulk substation to bulk substation and 4 145kv 1000kcmil solid dielectric cables between the bulk and each area substations.
Second- what contingency level should I design this for? I am currently thinking N-2 (2 circuits out) on both 330 and 110kv, as failures of underground cables take much more time to repair.
Third, though not really the scope of my question but still partly relevant- cable charging compensation shunt reactors should be placed on each cable bay or lumped and placed on the bus?
I have no reference to go by... I am open to any suggestions/critique. The substations will be GIS btw.