Underground cable

John165

Member
Location
New Mexico
Occupation
Journeyman
Do you need to sleeve under ground cable going under a slab? I thought that you did, but one of our guys says no. I can't find anything in the code.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
With correct depth you don’t have to sleeve by code , but why wouldn’t you anyway?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
300.5(C)
Underground Cables and Conductors Under Buildings. Underground cable and conductors installed under a building shall be in a raceway

(with exceptions)
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
300.5(C)
Underground Cables and Conductors Under Buildings. Underground cable and conductors installed under a building shall be in a raceway

(with exceptions)

I didn’t know it was a building..
 