underground conduit for boiler control, between 2 buildings each with own service

Status
Not open for further replies.

FREEBALL

Senior Member
Location
york pa usa
how do I bond a underground GRC between 2 buildings with separate services each building is fed with 600 amp 480v 3 phase 4 wire. I need to run a control conduit for the boiler. from one building to the other. I would like to use grc due to the parking lot/driveway load of tractor trailers. so can I use grc underground and stub up from 24 inches in pvc

thanx
jeff
 
how do I bond a underground GRC between 2 buildings with separate services each building is fed with 600 amp 480v 3 phase 4 wire.

I'm not an expert on this subject however I believe the underground GRC does not need to be bonded. You do need to run a ground wire through the conduit and bond it wherever the conduit terminates at each end as normal.
 
I've ran a lot of pvc on farms under roads with HEAVY traffic, etc. I've never had an issue as long as I had the depth required.
 