W wchild1520 Member Location Palm Springs Ca. May 14, 2013 #1 Are there any requirements for clearence from other utilities when installing underground conduit , I found cover requirements .
Are there any requirements for clearence from other utilities when installing underground conduit , I found cover requirements .
raider1 Senior Member Staff member Location Logan, Utah May 14, 2013 #2 There are no spacing requirements for underground raceways from other systems in the NEC. Check with the other Utility companies they may have local rules. Chris
There are no spacing requirements for underground raceways from other systems in the NEC. Check with the other Utility companies they may have local rules. Chris
H Hv&Lv Senior Member Location - Occupation Engineer/Technician May 14, 2013 #3 There are some in the NESC, but it probably doesn't apply to your installation...
Ponchik Senior Member Location CA Occupation Electronologist May 15, 2013 #4 As suggested you need to check with your local power company for clearances. Also make sure you call digalert before you do any digging.
As suggested you need to check with your local power company for clearances. Also make sure you call digalert before you do any digging.