Underground Conduit

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Have (2) concrete encased duct banks with (8) 5" conduits each. They are only being stubbed out for extension by others at a later date. Distance is about 45' for each run. I'm using spacer but are any other supports needed when turning up? A disconnect switch will be landed over the conduits by others at a later date. BTW it's FRE conduit.

1710761742598.png
1710761765026.png
1710761907279.png
 
Location
Columbus
Occupation
Master electrician, licensed contractor
Are you turning up in rigid? That gets heavy, you’ll want to to drive strut into the ground and the out horizontal strut to strap to
 