Underground DC conduit depth

Status
Not open for further replies.

electro7

Senior Member
Location
Northern CA, US
Occupation
Electrician, Solar and Electrical Contractor
I was wondering if I could get some help on depth for DC conduit 600V max.

We were unable to get to 18" of cover on some PV Source Circuits with maximum voltage of 600V in PVC Sch. 40 conduit..

In 300.5 would I be looking at Column 3 at a minimum cover of 12" with 2" of concrete on top of conduits?
 
Status