Re: underground duct banks
Originally posted by stanrat: So, aside from the fact that I'm the engineer . . . , what's my recourse?
I?m an engineer, too. This topic has come up several times in this forum. You can do a word search and find several related discussions. I have often stated that I essentially agree with the position you are now advocating.
But first, let?s talk code. B310.7 is not a code requirement. 310.77-86 apply to conductors rated over 2000 volts. So where in the enforceable sections of the code does it address the possibility that a 600 volt conductor might be in need of a de-rating due to the heat imposed upon it by nearby conductors in the same ductbank? Where? Nowhere, that?s where.
Here is how I resolve the issue in my own mind. If you calculate the load per 220, and if you look in 310.16 for a set of conductors that can handle the calculated load, you are OK. If you determine the existing load at an existing facility from measurement, and if you wish to determine if you have room to add more load, and if you look in 310.16 to see if the existing set of conductors can handle the ?measured plus newly added? load, you are NOT OK.
The difference comes from an (admittedly) weak argument, as follows:
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Premise A: The NEC 220 calculated load is higher than the true load that the facility will see in real life. This is a step toward conservatism, and helps us.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Premise B: The NEC 310.16 ampacities are lower than they should be, for use in underground ducts. This is a step away from conservatism, and works against us.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Conclusion: The two steps cancel each other out.</font>
<font size="2" face="Verdana, Helvetica, sans-serif">The weakness in this argument, of course, is that we do not know how much conservatism we gain on one hand, and lose on the other hand. By contrast, however, if you obtain your value of load from a measurement, the conservative step of Premise A vanishes. What is left is not sufficient.
Back to your question: What recourse do you have? You already know the answer to this question. You have a duty to the owner and to the future occupants of the facility, to create a design that is safe. If you think you are being pushed into an unsafe direction, your first recourse is to appeal to the owner, and your next recourse is to report the situation to the Authority Having Jurisdiction.