designer82
Senior Member
- Location
- Boston
I ran an underground ductbank ampacity calculation in ETAP.
Although the ductbank is very large with about 46 conduits, the calculation results are crippling.
It shows a 1200 Amp base ampacity cable derated to only about 400 Amps. So that's like a 67% derate.
We're already running 4 sets of 500Kcmil for 1200A feeders.
I'm thinking these underground ductbank ampacity calculations are too conservative and may just ignore it.
Any experience with this? Do these results seem reasonable?