S Scotty B. Member Jun 12, 2018 #1 I am installing a 350' long run of PVC, 240V single phase feeder underground. Am I permitted to put a quazite pull box somewhere in that run? There will be no splices in the pull box.
I am installing a 350' long run of PVC, 240V single phase feeder underground. Am I permitted to put a quazite pull box somewhere in that run? There will be no splices in the pull box.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Jun 12, 2018 #2 Yes, there is nothing in the code that either requires or prohibits that box.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Jun 12, 2018 #3 You can even bury it if you can comply with the exception in 314.29.
S Scotty B. Member Jun 12, 2018 #4 don_resqcapt19 said: Yes, there is nothing in the code that either requires or prohibits that box. Click to expand... That's what I thought, just wanted to make sure I wasn't missing something. Thank you