S sportzcoach Member Location Denver Occupation Electrical Contractor Oct 26, 2022 #1 I am running URD approximate 250 feet direct bury. feeding 200 amp service on house. what size Al URD do I need?
I am running URD approximate 250 feet direct bury. feeding 200 amp service on house. what size Al URD do I need?
ron Senior Member Location New York, 40.7514,-73.9925 Oct 26, 2022 #2 If no adjustment or correction factors are required, use Table 310.12 (NEC 2020).
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Oct 26, 2022 #3 sportzcoach said: I am running URD approximate 250 feet direct bury. feeding 200 amp service on house. what size Al URD do I need? Click to expand... Are you asking about voltage drop compensation? What is your current? Using the Southwire app with 150 amps I come up with 300 kcmil Al. Using the section Ron posted the minimum size would be #4/0.
sportzcoach said: I am running URD approximate 250 feet direct bury. feeding 200 amp service on house. what size Al URD do I need? Click to expand... Are you asking about voltage drop compensation? What is your current? Using the Southwire app with 150 amps I come up with 300 kcmil Al. Using the section Ron posted the minimum size would be #4/0.