I have a job installing a 24kw generator about fifty feet from the side of the house and meter. What is the best wiring method for this installation? I suppose I could use SEU for direct burial but what about the control cable? Or would PVC be best with all of the conductors in the same raceway?

Also, will I need a separate trench for the gas line?
 
Or would PVC be best with all of the conductors in the same raceway?
Definitely PVC, and possibly two, even though we're now allowed to put the control wiring in the feeder conduit.

Also, will I need a separate trench for the gas line?
That's totally up to the gas contractor, but I'd separate it.
 
Generac used to specify a separate conduit for the control wires, even though they shared a flex from the genny to a separate box.
 