We are designing a 3000A underground 480V cable run that will bring standby generator power into a building via an UG ductbank. The Neher-Mcgrath/Engineering Supervision method of sizing the cables was used. The cables are being connected to terminations that are rated for 75C. The cable itself has a 90C rating.
One group is insistent on installing a cable vault under the generator so the final 8 ft of the run can transition from the ductbank to the generator terminations in free air due to this area exceeding 75C in the calculations for the duct bank sweeping up into the generator slab. This group is firm that 75C cannot be exceeded anywhere in the run due to the 75C rating of the terminations (110.14 C)
Another opinion is the 310.14 A (2) Exception applies where the requirement for the higher ampacity can be ignored due to the length in question being under 10'.
I feel like the calculation method is being mixed with the table methods of determining ampacity but I'm having trouble determining the separation of the two. The 2017 NEC applies here.
One group is insistent on installing a cable vault under the generator so the final 8 ft of the run can transition from the ductbank to the generator terminations in free air due to this area exceeding 75C in the calculations for the duct bank sweeping up into the generator slab. This group is firm that 75C cannot be exceeded anywhere in the run due to the 75C rating of the terminations (110.14 C)
Another opinion is the 310.14 A (2) Exception applies where the requirement for the higher ampacity can be ignored due to the length in question being under 10'.
I feel like the calculation method is being mixed with the table methods of determining ampacity but I'm having trouble determining the separation of the two. The 2017 NEC applies here.