underground grounding conductor to multiple light poles

Status
Not open for further replies.

d-decherd

Member
Location
Illinois
We are looking at revising the wiring to an existing stadium lighting system.
All of the lighting poles are fed underground in conduit.
A typical lighting circuit has a 30 amp, 3 pole, 3 phase circuit breaker feeding a single pole.
There are four poles fed from one panelboard.
Each pole has its own 3 pole circuit breaker feeding the lights on the top of the pole.

There is one grounding conductor going from the panelboard to all of the poles.
The grounding conductor is tapped at each pole.
The wirenuts that are used to tap the grounding conductor are installed underground. These will have to be replaced.

Question:
Is there a provision in the code that requires that you bring a separate grounding conductor to each pole.
Example: Are you required to run a single grounding conductor with each 3 phase circuit?
 
250.122 Size of Equipment Grounding Conductors.

250.122 Size of Equipment Grounding Conductors.

I think I might have found the answer to my original question

250.122 Size of Equipment Grounding Conductors.
(C) Multiple Circuits. Where a single equipment grounding conductor is run with multiple circuits in the same raceway, cable, or cable tray, it shall be sized for the largest overcurrent device protecting conductors in the raceway, cable, or cable tray. Equipment grounding conductors installed in cable trays shall meet the minimum requirements of 392.10(B)(1)(c).
 