Is there another code article other than 300.5 (D) (3) that requires marking ribbon in the ditch. Have an inspector failing a install because there was not RED marking ribbon placed in the ditch over the conduit. The run is from a ground mounted solar array to the inverter. The wire is in ridged metallic conduit ( RMC ) at a depth of 12 inches which well complies with table 300.5. These conductors are not service conductors and do not meet any other requirement in 300.5 (D) (3).
 

Greentagger

Senior Member
Location
Texas
Occupation
Master Electrician, Electrical Inspector
I’ll take the bait. I agree with the OP that these are not service conductors,…………..but I’ll disagree that service conductors don’t require marking tape. Per 300.5(D)(3), isnt the verbage”are not encased in concrete”. What conductor insulation is rated for concrete encasement? Learn me guys. You have before. Thanks.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
I’ll take the bait. I agree with the OP that these are not service conductors,…………..but I’ll disagree that service conductors don’t require marking tape. Per 300.5(D)(3), isnt the verbage”are not encased in concrete”. What conductor insulation is rated for concrete encasement? Learn me guys. You have before. Thanks.
You are correct about the wording in 300.5(D)(3). I remember service conductors only needing to be in conduit to not need marking tape. Either way non service conductors need marking tape none of the time.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I’ll take the bait. I agree with the OP that these are not service conductors,…………..but I’ll disagree that service conductors don’t require marking tape. Per 300.5(D)(3), isnt the verbage”are not encased in concrete”. What conductor insulation is rated for concrete encasement? Learn me guys. You have before. Thanks.
The language in that section is poor as you are correct that you cannot directly buried service conductors in concrete. Also list item (4) should be a part of list item (1) and that is the only part that (4) applies to.

That being said, the parent text says, "Direct-buried conductors and cables". Nothing in 300.5(D) applies to conductors or cables in raceways. The rule only applies to conductors or cables that are placed directly in the earth.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Thx Don
so would this apply to a PV array, Genset, etc that was an SDS then?

~RJ~
It only applies to directly buried service conductors that are installed by other than the utility. "Service lateral" conductors do not require the ribbon, but "service conductors, underground" do require it. An SDS is not a service and does not have service conductors.

Note that often project specifications will require the warning ribbon.
 

anbm

Senior Member
Location
TX
Occupation
Designer
It only applies to directly buried service conductors that are installed by other than the utility. "Service lateral" conductors do not require the ribbon, but "service conductors, underground" do require it. An SDS is not a service and does not have service conductors.

Note that often project specifications will require the warning ribbon.
I am wondering why someone would install service conductors without conduit for underground run?
 

packersparky

Senior Member
Location
Wisconsin
Occupation
Inspector
Thx but..... that's rather confusing, considering it stands for Separately Derived SERVICE Don

~RJ~
Separately Derived System. An electrical source, other than a service, having no direct connection(s) to circuit conductors of any other electrical source other than those established by grounding and bonding connections. (CMP-5)
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Thx but..... that's rather confusing, considering it stands for Separately Derived SERVICE Don

~RJ~
System and not service. Service conductors are those conductors that connect directly to the power company system. Conductors that connect to any other system, are not service conductors.
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
I've been installing these regardless of minimum requirements, I've been using the traceable type. If someone digs up one of mine they've got no excuse. I've seen too many damaged pipe or conductors from guys digging. Had one guy excavating hit one in conduit hooking it with a backhoe and ripped meter right off the building and conductor off the pole and snapped wire in half. Close to 500ft of conductors. They got 811 marking but that only covers the utility side not private feeders. Anything after service drop is private according to 811.
 