Underground receptacle

Status
Not open for further replies.

codequestion

Banned
Location
MD, USA
Engineering plans call for underground receptacle without GFI protection. Anyone have any idea as to who sell them or where in NEC underground receptacle article/section would be?
 
The location of the receptacle along with voltage and amperage would need to be known for starters.

JAP>
 
I see a risk that a damaged power cord plugged in could provide an air exit path, allowing the water level to rise at least to the height of the cord sheath break.
 
I see a risk that a damaged power cord plugged in could provide an air exit path, allowing the water level to rise at least to the height of the cord sheath break.

:lol: Which is exactly what happens to any underground J-box installation eventually, devices installed or not.

JAP>
 
I see a risk that a damaged power cord plugged in could provide an air exit path, allowing the water level to rise at least to the height of the cord sheath break.
I don't follow you, the "diving bell" design doesn't depend on any sort of sealing around the power cord.

Cheers, Wayne
 
I don't follow you, the "diving bell" design doesn't depend on any sort of sealing around the power cord.

Cheers, Wayne
The diving bell effect requires that the space inside the bell be airtight. A damaged cord could provide an air leak to the outside.

Sent from my XT1585 using Tapatalk
 
A diving bell doesn't need to be water tight below the connections. Diving bells are by their very nature open at the bottom.
 
A diving bell doesn't need to be water tight below the connections. Diving bells are by their very nature open at the bottom.
Take a diving bell and run a hose from the inside to any point outside in open air and all the air will come out.
If the end of the hose is far enough down underwater then the air will not escape. (If the hose starts out full of water then as long as the top end is below the top surface of the bell you may also be OK?)

Sent from my XT1585 using Tapatalk
 
If I follow the idea correctly, then if the cord jacket is damaged both inside the diving bell space, and outside at a greater height, but is otherwise intact, it could provide an enclosed path for air to escape. In which case when flooded the water in the diving bell will rise up to the height of the interior damage.

Seems like this could be prevented in one of two ways: ensure the jacket inside the diving bell is undamaged, or put a hole in the jacket at its bottom-most point, so that the jacket floods there and doesn't allow air to pass. Maybe this second way is not advised (although my sump pump came with a plug with an air relief opening on it, so perhaps it is not so crazy).

Agreed?

Cheers, Wayne
 