H Hfalz1 Member Location Houston, Tx. Occupation Electrician Jul 26, 2017 #1 I'm trying to find the min. and max distance between underground feeders and communication cables in conduit. Anyone know what code section i should be looking at? Also burial depths.
I'm trying to find the min. and max distance between underground feeders and communication cables in conduit. Anyone know what code section i should be looking at? Also burial depths.
ActionDave Chief Moderator Staff member Location Durango, CO, 10 h 20 min from the winged horses. Occupation Licensed Electrician Jul 26, 2017 #2 Table 300.5 for burial depths. There is no separation requirements.
steve66 Senior Member Location Illinois Occupation Engineer Jul 26, 2017 #3 And I don't think there is any minimum depth for the communications conduits.