NEC User
Senior Member
- Location
- Marlboro, NJ, USA
I?m trying to size the service entrance conductors for a building renovation.
For a building renovation, I calculated a design load of 75 KW (94 KVA)
S = sqrt(3) x I V
94,000 = 1.732 x I 208
I = 261 Amps
Per NEC, we size wires to accommodate 25% spare capacity.
Total Amperes (I) with 25% spare capacity = 261 x 1.25 = 326 Amps
Using NEC Table 310.15 (B) (16) 75 degree column the following cables and conduit sizes are required
4#400 KCMIL in one (1) 4? Conduit
The utility company responded saying that they are going to provide 4#2 cables in the underground service.
How did they get 4#2 from the information I provided? They didn't indicate any transformer prior to the building.
For a building renovation, I calculated a design load of 75 KW (94 KVA)
S = sqrt(3) x I V
94,000 = 1.732 x I 208
I = 261 Amps
Per NEC, we size wires to accommodate 25% spare capacity.
Total Amperes (I) with 25% spare capacity = 261 x 1.25 = 326 Amps
Using NEC Table 310.15 (B) (16) 75 degree column the following cables and conduit sizes are required
4#400 KCMIL in one (1) 4? Conduit
The utility company responded saying that they are going to provide 4#2 cables in the underground service.
How did they get 4#2 from the information I provided? They didn't indicate any transformer prior to the building.