3-49 Log #2232 NEC-P03 Final Action: Reject
(300.5(D)(3))
____________________________________________________________
Submitter: Donald A. Ganiere, Ottawa, IL
Recommendation: Revise as follows:
(3) Service Conductors. Underground service conductors that are not encased
in concrete and that are buried 450 mm (18 in.) or more below grade shall have
their location identified by a warning ribbon that is placed in the trench at least
300 mm (12 in.) above the underground installation.
Substantiation: The potential hazard from a “dig-in” accident is not changed
by the method used to install the conductors. If service conductors installed in
a trench present a hazard, then so do service conductors installed by directional
boring or other “trenchless” methods. The warning ribbon requirement should
apply to all underground service conductors or to none of the underground
service conductors. The panel should not consider the additional costs required
to install the warning ribbon when “trenchless” installation methods are used.
The only consideration should be the safety of the system, and if trenched in
service conductors require a warning ribbon for safety reasons, then so do
service conductors installed using other methods of installation.
Panel Meeting Action: Reject
Panel Statement: The only way to install a warning ribbon 12-inches above a
bored hole containing service conductors would be to drill an additional hole
with the ribbon inserted in the hole and pulled through from one location to
another or to dig a trench to a depth 12-inches above the cable. In addition,
since the ribbon would be installed in a drilled hole, the inspector would not
be able to verify the depth of the ribbon as being 12-inches above the service
conductors.
Number Eligible to Vote: 13
Ballot Results: Affirmative: 12 Negative: 1
Explanation of Negative:
CASPARRO, P.: See my explanation of negative vote on Proposal 3-38.