Is there an Article that addresses Art 725 or Art 800 burial depth or protetion emerging from ground ??
 

Another C10

Electrical Contractor 1987 - present
Location
Southern Cal
Occupation
Electrician NEC 2020
The only thing I'm seeing is 830.47(C) other than that I would presume the rules on burial apply as they would with standard power lines noted on 300.5
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
IMO it goes back to manufacturers specs.
some manufacturers say bury at 12” deep.

I‘ve never figured out why though..

I would say in a field as long as its deeper than a bottom plow, and in a yard at least deeper than a good plugger..
 

PaulMmn

Senior Member
Location
Union, KY, USA
Occupation
EIT - Engineer in Training, Lafayette College
I would say in a field as long as its deeper than a bottom plow, and in a yard at least deeper than a good plugger..
Don't forget a garden spade, shovel, or enthusiastic Roto-Tiller. Route of the line should also be marked or photographed while under construction to prevent fun when digging a hole for a new tree...
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
Here in Oregon they adopt codes statewide and actually include the IEEE C2-2017/NESC along with the NEC and in this oddball case where something is not covered in the NEC but is in the NESC they go by NESC which I believe is 24 inches, it came up on a project once and left a lasting memory.

 