There are pin terminals to accomplish what I believe you are doing.
https://commerce.ilsco.com/e2wShoppingCatalog.aspx?parentId=3100012329
Who knows,,,, he may be looking for some ammo to scold someone for what They are doing.
JAP>
Not scolding anyone, just writing an electrical deficiencies report, I also found 110.14 A
I think 110.14(A) covers it. That looks like a violation to me.
I think 110.14(A) covers it. That looks like a violation to me.
I agree with that also.
JAP>
I dont actually think 110.14(A) covers it. To me that is talking about not damaging the conductor while making the connection. When you trim off strands you are changing/damaging the concductor prior to that. I would go with something like 240.4 - the conductor is now smaller than XX size and (presumably) not protected at its ampacity. If one could document/prove the size of the "new" conductor after the strands were removed, and it was done without damaging the remaining strands, I wouldnt have a problem with it if it was protected at its ampacity.
That's a good one too.
I'll agree with that one also.
Jap>
there is no specific code that prohibits this. however, when you remove strands from a conductor you have made it a different size conductor which has a different ampacity.
I agree in principle, now show me an inspector that will buy it.I dont actually think 110.14(A) covers it. To me that is talking about not damaging the conductor while making the connection. When you trim off strands you are changing/damaging the concductor prior to that. I would go with something like 240.4 - the conductor is now smaller than XX size and (presumably) not protected at its ampacity. If one could document/prove the size of the "new" conductor after the strands were removed, and it was done without damaging the remaining strands, I wouldnt have a problem with it if it was protected at its ampacity.
I agree in principle, now show me an inspector that will buy it.![]()
That is what I was talking about. If you can prove what the reduced CSA is after trimming and it is still above needed conductor ampacity then I see no reason it won't work. May appear as "hack" but in principle should still work.I'm not sure what you mean, but I have reduced the size of large feeders from PV systems a long way from services right before connecting to a disco when the reduced size was sufficient for the required ampacity but not for voltage drop. Built and passed inspection. Not by trimming strands, though, if that's what you mean.