harritr1
Member
- Location
- Houston, TX
I have come across some cables that I believe to be undersized but I wanted to see if maybe there is some weird industry rule/exception I am just unaware of.
So I have a 1200A automatic transfer switch upstream of 6 single conductor 750kcmil CU cables (2 per phase) in underground conduit with an 800A switch at the end. With my calculations I don't see how these cables are protected by the ATS since their ampacity does not go above 1200A.
Am I missing something here or is there something in the code about these cables not needing to be protected by the ATS?
Any comments or tips are helpful
So I have a 1200A automatic transfer switch upstream of 6 single conductor 750kcmil CU cables (2 per phase) in underground conduit with an 800A switch at the end. With my calculations I don't see how these cables are protected by the ATS since their ampacity does not go above 1200A.
Am I missing something here or is there something in the code about these cables not needing to be protected by the ATS?
Any comments or tips are helpful