Chrisjohnson
Member
- Location
- Ashland OH
- Occupation
- Maintenance electrician
I'm the "new" electrician at a small factory in Central Ohio. Our production lines use molten salt baths to cure rubber and silicone extrusions. I don't believe the controls are properly sized. I clamped the conductors ( 6 circuits, 480v 3phs) @ 26.5 amps. The contactor is rated @ 40a the overcurrent bkr is 40a and the wire is #8. The devices are operated 24 hrs a day to maintain the molten condition of the salt and they are very warm to the touch. I don't believe continuous duty derating or 60% capacity of the bkr is being applied properly....am I off base?