If that is true, then there is no need to run a neutral at all. Call it a 480 volt service, and not a 480/277, and save yourself a wire.jdr said:there is only 3ph load.
charlie b said:If that is true, then there is no need to run a neutral at all. Call it a 480 volt service, and not a 480/277, and save yourself a wire.
Ragin Cajun said:A 2000A service needs ~ 7 - 500MCM/phase for a total of 3500mcm. Per table 250.66 this is >1100 MCM so the grounded conductor should be 3/0?
No, 250.24(C) requires it to be brought to the servce equipment. From there you run it only if needed.
charlie b said:If that is true, then there is no need to run a neutral at all. Call it a 480 volt service, and not a 480/277, and save yourself a wire.
You have to read all of the section.A 2000A service needs ~ 7 - 500MCM/phase for a total of 3500mcm. Per table 250.66 this is >1100 MCM so the grounded conductor should be 3/0?
Don(1) Routing and Sizing This conductor shall be routed with the phase conductors and shall not be smaller than the required grounding electrode conductor specified in Table 250.66 but shall not be required to be larger than the largest ungrounded service-entrance phase conductor. In addition, for service-entrance phase conductors larger than 1100 kcmil copper or 1750 kcmil aluminum, the grounded conductor shall not be smaller than 12 1/ 2 percent of the area of the largest service-entrance phase conductor. The grounded conductor of a 3-phase, 3-wire delta service shall have an ampacity not less than that of the ungrounded conductors.
2000 amps will take 6 sets ot 500kcmil or 5 sets of 600kcmil. In either case the total is 3000 kcmil per phase. 12.5% of 3000 kcmil is 375 kcmil. 1/0 is 105.6 kcmil so 5 1/0 will have more than the required area.I did the math and figured it at 2/0 per raceway...calculations are not my strength. Can you show me where I went wrong?
infinity said:Why 7 sets? 2000amps/380amps=5.26 or 6 sets.
infinity said:There is such a thing as a 3 wire Delta service which could be used if there are no 277 volt loads requiring a neutral.
don_resqcapt19 said:Ragin,
You have to read all of the section.
Don
don_resqcapt19 said:RC,
In both of the last two cases, a 1/0 in each raceway is more than the required 12.5%. 310.4 is the only reason that you need a 1/0 in each raceway.
Don
don_resqcapt19 said:RC,
You only need 12.5% of the total of the largest set of phase conductors. If you have 10 sets of 500kcmil, you have a total of 5000kcmil. 12.5% of that is 625kcmil. That is the total of all 10 grounded conductors. If it wasn't for the 1/0 minimum size rule in 310.4 you could install 10 #2s and be in compliance with the 12.5% rule.
Don