Undersized SSBJs - What to do?

Sider

Member
Hi all,

I'm part of the design team for a new high rise. It has 480V distribution stepping down to 208/120 in each electrical closet. There are 2-3 transformers per closet, so we're talking about a sizable number of transformers. The building is approaching completion and is planning to open in a few months.

Well, inspections have rolled around, and the AHJ found all transformer secondary SSBJs were sized as EGCs. In some cases the sizes were correct purely by coincidence, but for most transformers the SSBJ is exactly one size too small. The client is now looking for the quickest code-compliant solution.

Key points:
- This project is under the 2011 NEC.
- N-G bond is at the transformer via manufacturer-provided jumper.
- SSBJ is connected from the transformer ground terminal bus to the panelboard ground terminal bus.
- Secondary protection is the MCB of the downstream panel. Secondary feeder is run in 4-5 feet of FMC followed by 10-15 feet of EMT. There are three 90-degree bends: the FMC termination at the transformer, plus two 90s for the overhead transition. I've attached a rough sketch.
- Typical wire fill in secondary conduit is between 20% and 28%.

Some questions:
1. Is it possible to reliably pull a new ground wire in the same conduit without damaging the insulation on the existing bundle? Or would you rather pull the whole feeder out and re-bundle? The contractor has already looked at pulling out the whole feeder and found it would take 2-3 months at ~4-6 hours per transformer.
2. 250.30(A)(2) allows nonflexible metal raceway to be used as a SSBJ, but we have FMC for the final few feet of the run. Is it NEC-compliant to jumper over the FMC portion using a grounding clamp and correctly-sized wire outside the conduit, provided the jumper is less than 6 feet? I had trouble finding anything for or against this.
3. The AHJ briefly considered allowing the SSBJs to remain as-is, although I don't know if that went anywhere. What are the dangers realistically posed by an undersized SSBJ? My understanding is that in the event of a fault between the transformer and the secondary OCP, the SSBJ needs to survive long enough for the primary OCP to trip, since the secondary isn't seeing the fault. And if the fault is past the secondary OCP, then the SSBJ is just a continuation of the EGC path, so a larger SSBJ wouldn't appear to matter. Has anyone experienced an issue stemming from an undersized SSBJ?

And maybe the most important question - in my shoes (or the contractor's), how would you approach this?

Thanks.
 

Attachments

  • TX_Install.jpg
    TX_Install.jpg
    1.3 MB · Views: 15
  • TX_Install.jpg
    TX_Install.jpg
    1.3 MB · Views: 15
Agree with infinity, I've never seen a factory installed N-G bond. There is normally a flexible strap that bonds the core that is often mistaken as a N-G bond (a continuity check would confirm)
What size conductors are you looking at?
 
Agree with infinity, I've never seen a factory installed N-G bond. There is normally a flexible strap that bonds the core that is often mistaken as a N-G bond (a continuity check would confirm)
What size conductors are you looking at?
Yes, I may be making this exact mistake. I haven't seen it in the flesh; I just know the inspector's report said the SBJ and GEC were both sized correctly, and that the N-G bond was at the transformer. It was just the SSBJ out from the transformer to the MCB of the downstream panel that he (rightly) had a problem with.

The phase conductor sizes range from 8 AWG for the 15 kVA all the way up to 600 kcmil for the 112.5 kVA. The ground wires range from 8 AWG to 1/0 AWG.
 
Shouldn't be a problem to pull one out and the other one right in.
Thanks for the feedback. That was my first suggestion, of course. There was contractor pushback, namely that they were worried about nicking the insulation and would need to pull out the whole bundle to do it right (at a pace of 4 hours per transformer). My instinct is that they're exaggerating the difficulty, but I'm not out in the field and don't want to dismiss that concern without checking in on it.
 
Thanks for the feedback. That was my first suggestion, of course. There was contractor pushback, namely that they were worried about nicking the insulation and would need to pull out the whole bundle to do it right (at a pace of 4 hours per transformer). My instinct is that they're exaggerating the difficulty, but I'm not out in the field and don't want to dismiss that concern without checking in on it.
I agree that they're exaggerating the difficulty. As long as they properly tape up the bare conductors noting is going to get nicked or damaged. They can even use some wire lube on the larger conductors to make it slide through easier.
 
I managed to get a photo of a typical transformer condition, and confirmed that the X0 is tied to the transformer ground bus by a wire. So the N-G bond is definitely in the transformer.

As for the SSBJ: The attached images show the point where both sets (primary top, secondary bottom) enter the transformer via the flex connections. The SSBJ to be re-pulled is the ground in the bottom conduit. Does that look doable?
 

Attachments

  • wirefill_tx.PNG
    wirefill_tx.PNG
    729.4 KB · Views: 19
  • wirefill_tx_2.PNG
    wirefill_tx_2.PNG
    578.3 KB · Views: 18
Is there an angle connector on the outside with a removable cover? No problem to pull out the old and pull in the new at the same time.
It's the screw-on type. Photos attached.
 

Attachments

  • tx_outside.PNG
    tx_outside.PNG
    675.1 KB · Views: 17
  • tx_outside_2.PNG
    tx_outside_2.PNG
    1 MB · Views: 16
You take the cover off and you wouldn't even need to pull the new wire around the bend. Is someone saying that this is difficult?
 
Someone is, in fact, saying that this is difficult. Sigh 🤦‍♂️
Thanks a lot - I really appreciate the feedback.
 
Someone is, in fact, saying that this is difficult. Sigh 🤦‍♂️
Thanks a lot - I really appreciate the feedback.
Just curious who is on the hook to pay for this error? The electrical contractor should have known what size of required for the SBJ.
 
That'll be settled by people well above my paygrade ;)
This is a very common engineering mistake. I've seen this on many jobs. How's this look?


20220210_070105 (2).jpg

I ended up fixing the entire table for them after they had already wired about 30 transformers incorrectly.

GEC Table Corrected.jpg
 