We got called over a 12gauge 5 core cable to an A/C unit FLA 16A per phase LRA 80A,40A breaker,inspector said we'd have to upsize the cable,consumer mains,i disagreed,until recently,OCPD was allowed to exist at the panel or the unit,the breaker only giving s/c protection,unit said,Carrier Airconditioning Corporation,Newark New Jersey,use 40A breaker,guy got us to change it to 20a,kept nuisance tripping,so my daughter changed it back,Unit had been working fine for 25 years till Mrs Possum came along,causing corrosion on the condenser,a local HVAC guy repaired the unit,removed the animals,put a nest box in a tree for them,then the inspector comes along.What do you guys think?