menoknow
Member
- Location
- Washington State
- Occupation
- Electrician
Long story short I am currently hooking up power for some new manufacturing equipment in Washington State. Just finished hooking the first (4) production lines up to power with (4) more on a boat on the way here. However I have a bit of a crazy idea. I've been monitoring the current draw for over a month as I've been connecting these to power and they are drawing way under the nameplate rating. Significantly under the nameplate value. The nameplate value of the largest piece of equipment in one of the production lines is 250 amps, but the entire line consisting of (6) different pieces of equipment is only drawing 25 amps at 480V. Currently the largest piece of equipment is hooked up with 350kcmil aluminum conductors, but I was thinking on the future installations is there any reason I can't underpower some of the equipment. Say hook the largest one up with 3awg copper conductors on a 100 amp breaker?
There is a 75HP motor in that piece of equipment, but I see absolutely no inrush current on the power monitor. (3) have been hooked up and running at full tilt for almost 2 weeks now, and my monitor has not detected a peak over 80 amps. I'm assuming this has to do with the beast of a frequency drive controlling the motor, but it seems a little ridiculous to have to fully size these circuits going by the NEC.
I don't think it would be a safety concern as the wire would be fully protected whatever ampacity I choose as long as the breaker is properly sized. Anyone have any thoughts on this? Would I be violating the NEC if I were to do this? in the past I've hooked up equipment rated at 225 amps on a 200 amp circuit and pass inspection with flying colors.
There is a 75HP motor in that piece of equipment, but I see absolutely no inrush current on the power monitor. (3) have been hooked up and running at full tilt for almost 2 weeks now, and my monitor has not detected a peak over 80 amps. I'm assuming this has to do with the beast of a frequency drive controlling the motor, but it seems a little ridiculous to have to fully size these circuits going by the NEC.
I don't think it would be a safety concern as the wire would be fully protected whatever ampacity I choose as long as the breaker is properly sized. Anyone have any thoughts on this? Would I be violating the NEC if I were to do this? in the past I've hooked up equipment rated at 225 amps on a 200 amp circuit and pass inspection with flying colors.