underslabed floor box and gfci ?

Status
Not open for further replies.

allenwayne

Senior Member
If the wire in a under slabbed floor box must meet requirements for a wet location,then shouldn`t that cicuit be gfci protected ???
 
Re: underslabed floor box and gfci ?

I don't see why it would. The GFCI protection is to protect the 'user', someone who has plugged something into the receptacle. Why would it matter if the receptacle were mounted in the floor or in the wall? The location of the receptacle should matter in determining if it needs GFCI protection, not the wiring method.
 
Re: underslabed floor box and gfci ?

If you're wanting to use the 0" burial depth in column 4 of 300.5 it will.
Otherwise, no!

Dave
 
Re: underslabed floor box and gfci ?

Dave,
The rule in Column 4 of Table 300.5 only applies to residential occupancies, so if this is not residential, then the GFCI would not be required for "0" burial depth.
Don
 
Re: underslabed floor box and gfci ?

Even if this is a dwelling GFCI protection would not be required. All raceways listed in table 300.5 are permitted with 0" cover under a building.
 