Ohms law
Senior Member
- Location
- Sioux Falls,SD
This is perfect, I was just trying to understand this whole 225.30 section. I had a question about disconnecting means. If you read 225.31 then read 225.32 ex.1 it seems to me it is saying you don't need a main breaker panel for a disconnect you could get away with a main lug panel in detached garage fed from house. Ex. 1 is saying under single management, as in the homeowner. Right?If you install a subpanel (or any other type of OCPD in the supply conductors, with the exception of a supplementary OCPD) then the supplying conductors would be a feeder... so the exception would not apply.