My question is regarding your every day 10k AIC rated residential equipment. ,
This is the scenario- Say you have a bolted fault line to line on a 20 amp 2 pole 240v circuit. Modern Siemens plug in breakers. I have seen recently that in this situation the 20 amp breaker does not trip but the main did.
Branch and Main same brand and 10k
Is this common?
Does the available fault current play part in this?
The service is only about 8' from the utility tranny. I would assume the available fault current could be greater than 10k which our utility CO states is max for Single Fam res.
This is the scenario- Say you have a bolted fault line to line on a 20 amp 2 pole 240v circuit. Modern Siemens plug in breakers. I have seen recently that in this situation the 20 amp breaker does not trip but the main did.
Branch and Main same brand and 10k
Is this common?
Does the available fault current play part in this?
The service is only about 8' from the utility tranny. I would assume the available fault current could be greater than 10k which our utility CO states is max for Single Fam res.