Hello, I'd like to double check I understand and am applying the NEC correctly for my situation after searching through some threads here.
I have an existing 480V/50A breaker that feeds an existing distribution system:
Transformer (no info)
Client wants to add 4x 480V/18.1A/15KW (not sure how they got those amps from the KW rating, that's the info I was provided) space heaters on a new 480V panel. Those are continuous per 424.3(B), so I'm using 3#8+1#10G for each on a 60A non-fused disconnect, fed from individual 480V/40A breakers based on 125% of the 15KW/480V.
From there it seems pretty obvious the 50A breaker feeding the system needs to be upsized if I had to have a 160A panel, but it's a 100A frame breaker. The existing system was not designed this way though, and they used 30A breakers for 7.5KW heaters (125% checks out) in a 30A panel.
Am I missing something that would let me size the new panel lower than a multiple >1 of the branch circuits' rating? Existing panel was done in 1996.
I have an existing 480V/50A breaker that feeds an existing distribution system:
Transformer (no info)
120/208/3ph Panel
Subfed 120/208/3ph LP on 2 pole 30A breaker
30A Fused Disconnect feeding 480V/30A/3ph panelClient wants to add 4x 480V/18.1A/15KW (not sure how they got those amps from the KW rating, that's the info I was provided) space heaters on a new 480V panel. Those are continuous per 424.3(B), so I'm using 3#8+1#10G for each on a 60A non-fused disconnect, fed from individual 480V/40A breakers based on 125% of the 15KW/480V.
From there it seems pretty obvious the 50A breaker feeding the system needs to be upsized if I had to have a 160A panel, but it's a 100A frame breaker. The existing system was not designed this way though, and they used 30A breakers for 7.5KW heaters (125% checks out) in a 30A panel.
Am I missing something that would let me size the new panel lower than a multiple >1 of the branch circuits' rating? Existing panel was done in 1996.