I am trying to understand the differences between the different Medium Voltage short circuit ratings for different medium voltage equipment.
For MV breakers I understand there are 3 different ratings called the Close & Latch (momentary), interrupting, and short time short circuit currents. I understand the close & latch to be the maximum first cycle asymmetrical short circuit current which is usually listed as a total RMS value or a peak value. I understand the momentary rating to be the short circuit rating at 3,5,8 cycles etc.. where the breakers interrupting time is at which the breaker interrupts the current. This is a maximum permissable value of current the breaker can interrupt at a given cycle time. I'm not quite sure if I understand what the short time rating is? Is this a rating that the breaker can withstand for a given time while a device upstream, or downstream is responsible for clearing the fault?
For MV Load Break switches I understand these switches to have (2) different ratings. For older switces I have seen them listed as "fault closing" and "momentary" however for newer switches I have seen them listed as "Fault Closing (momentary)" and "Rated Short-Time current" Can someone please explain these two different ratings for an MV switch and why newer switches seem to have different terminology for the ratings?
Are there any good references for understanding these ratings and how they are applied?
For MV breakers I understand there are 3 different ratings called the Close & Latch (momentary), interrupting, and short time short circuit currents. I understand the close & latch to be the maximum first cycle asymmetrical short circuit current which is usually listed as a total RMS value or a peak value. I understand the momentary rating to be the short circuit rating at 3,5,8 cycles etc.. where the breakers interrupting time is at which the breaker interrupts the current. This is a maximum permissable value of current the breaker can interrupt at a given cycle time. I'm not quite sure if I understand what the short time rating is? Is this a rating that the breaker can withstand for a given time while a device upstream, or downstream is responsible for clearing the fault?
For MV Load Break switches I understand these switches to have (2) different ratings. For older switces I have seen them listed as "fault closing" and "momentary" however for newer switches I have seen them listed as "Fault Closing (momentary)" and "Rated Short-Time current" Can someone please explain these two different ratings for an MV switch and why newer switches seem to have different terminology for the ratings?
Are there any good references for understanding these ratings and how they are applied?