Need help in finding appropriate paragraphs in NEC or other regulatory documents.
We are building machine, which is designed and labeled for three phase 208VAC electric power supply. One of the components on the machine is a pump. Nameplate on the motor of this pump is showing only 230/460 Volt, but not 208 Volt. In the past pump manufacturer was providing motor nameplate with 208-230/460V rating. When, we asked them to provide new motor nameplate, answer was that they have switched to premium efficiency motors, which are rated 230/460V.
Is it OK to use component that is rated higher than voltage of the circuit, where it will operate. Paragraph 110.4 saying that it "shall be not less than nominal voltage". Nothing is said about opposite. During testing measured motor current is higher than one shown on motor nameplate, 37.3A vs. 34A. Motor service factor is 1.00. Based on nameplate information motor load is 110%.
My feeling is that if machine as whole rated for 208 volts, then each component must have this rating. Can anyone point me to appropriate regulatory documents on these matters.
Thank you,
PaulBr.
We are building machine, which is designed and labeled for three phase 208VAC electric power supply. One of the components on the machine is a pump. Nameplate on the motor of this pump is showing only 230/460 Volt, but not 208 Volt. In the past pump manufacturer was providing motor nameplate with 208-230/460V rating. When, we asked them to provide new motor nameplate, answer was that they have switched to premium efficiency motors, which are rated 230/460V.
Is it OK to use component that is rated higher than voltage of the circuit, where it will operate. Paragraph 110.4 saying that it "shall be not less than nominal voltage". Nothing is said about opposite. During testing measured motor current is higher than one shown on motor nameplate, 37.3A vs. 34A. Motor service factor is 1.00. Based on nameplate information motor load is 110%.
My feeling is that if machine as whole rated for 208 volts, then each component must have this rating. Can anyone point me to appropriate regulatory documents on these matters.
Thank you,