Theres this breaker in an mcc that is 50 amps instantaneous, it has settings on at the 'E' level that is about 350 amps. This motor keeps tripping on start up periodiocally but not all the time. Check everything else out but couldn't find any other problems.
It was decided to increase the setting to the next level, 'F'. I had some concerns about this being too much reading NEC 430.52 (3) exeception 1 max is 1300 percent. ALSO THE TABLE 430.52 under instantaneous trip breaker , but according to the manufacturers 'code' on the motor the code letter is 'G', which im told is to correspond to the breakers setting level which would be 2 levels above where it was originally set. they appear to go up at 50 amp increments from the 350 setting.
This is a 25 hp flc 29 amp motor , i think squirel cage. D series
Am I reading this wrong, is this what the settings are to let the motor start without tripping the breaker, ?? When I do the math 29 X 13= 377 amps . It just looks like that would be too much. Please help.
Thanks.
It was decided to increase the setting to the next level, 'F'. I had some concerns about this being too much reading NEC 430.52 (3) exeception 1 max is 1300 percent. ALSO THE TABLE 430.52 under instantaneous trip breaker , but according to the manufacturers 'code' on the motor the code letter is 'G', which im told is to correspond to the breakers setting level which would be 2 levels above where it was originally set. they appear to go up at 50 amp increments from the 350 setting.
This is a 25 hp flc 29 amp motor , i think squirel cage. D series
Am I reading this wrong, is this what the settings are to let the motor start without tripping the breaker, ?? When I do the math 29 X 13= 377 amps . It just looks like that would be too much. Please help.