I have two current carrying conductors that need to be upsized to accommodate for voltage drop. I have only one equipment grounding conductor. I am upsizing current carrying conductors from #12 (20amp) to #6 (this is a 480V street lighting circuit that travels very far). To upsize my equipment grounding conductor properly do I use the ratio of increased circular mils of one of the conductors or both?
Option A
26251 mils (#6) divided by 6530 mils (#12) = 4.02
6530 mils x 4.02 = 26,251 mils (#6 awg required for ECG)
Option B
26251 mils (#6) times 2 conductors = 52502 divided by 6530 mils (#12) = 8.04
6530 mils x 8.04 = 52,502 mils (#2 awg required for ECG)
It doesn't seem logical that the single ground wire of the same size as the conductors could carry enough current back to the breaker when it took two conductors to get enough amperage over the distance in the first place. #2 awg EGC seems realistic.
Thanks in advance for the help