New member here with a question on Parallel Cable Runs
Let's say we have a 480VAC, 3-Phase, 15HP Motor, 550ft Cable Length, 75C Cable Rating, P.F. of 0.85, Copper Cable, and Temp Correction Factor of 1.
Using this information, and NEC430.250 I am seeing an FLA of 21[A].
Multiplying the FLA * 1.25 and using TableNEC240.6 I see a recommended upstream breaker size of 30A.
For Cable size based on Ampacity: Multiplying (UpstreamBreakerSize * TempCorrectionFactor) = (30A * 1) = 30 and using TableNEC310.16 i see a cable size of 10AWG
For Cable size based on 3%VoltageDrop: ( Sqrt(3) * 12.9 * CableLength * FLA) / CopperCM ) It appears 6AWG gives me 2.05%
Chosen cable size is the larger of the two above, so 6AWG.
Sorry for the long setup.
My question is a 2-parter:
1. Would having two parallel runs (same length and cable size per parallel run) change the formula for Cable Sizes as shown below?
New Cable Size Based on Ampacity: (UpstreamBreakerSize * TempCorrectionFactor) / NumberofParallelRuns and use TableNEC310.16 to get 14AWG per run
New Cable Size Based on 3%VD: ( Sqrt(3) * 12.9 * CableLength * FLA / NumberofParallelRuns) / CopperCM ) to get 10AWG at VD 2.59%
2. How would this affect upstream breaker size? Normally the cable needs to be sized to handle the full breaker ampacity. I would think that lowering the gauge of the cable would break this rule.
Let's say we have a 480VAC, 3-Phase, 15HP Motor, 550ft Cable Length, 75C Cable Rating, P.F. of 0.85, Copper Cable, and Temp Correction Factor of 1.
Using this information, and NEC430.250 I am seeing an FLA of 21[A].
Multiplying the FLA * 1.25 and using TableNEC240.6 I see a recommended upstream breaker size of 30A.
For Cable size based on Ampacity: Multiplying (UpstreamBreakerSize * TempCorrectionFactor) = (30A * 1) = 30 and using TableNEC310.16 i see a cable size of 10AWG
For Cable size based on 3%VoltageDrop: ( Sqrt(3) * 12.9 * CableLength * FLA) / CopperCM ) It appears 6AWG gives me 2.05%
Chosen cable size is the larger of the two above, so 6AWG.
Sorry for the long setup.
My question is a 2-parter:
1. Would having two parallel runs (same length and cable size per parallel run) change the formula for Cable Sizes as shown below?
New Cable Size Based on Ampacity: (UpstreamBreakerSize * TempCorrectionFactor) / NumberofParallelRuns and use TableNEC310.16 to get 14AWG per run
New Cable Size Based on 3%VD: ( Sqrt(3) * 12.9 * CableLength * FLA / NumberofParallelRuns) / CopperCM ) to get 10AWG at VD 2.59%
2. How would this affect upstream breaker size? Normally the cable needs to be sized to handle the full breaker ampacity. I would think that lowering the gauge of the cable would break this rule.