Understanding Parallel Cable Run Impact on Calculations

TacoEngineer

Member
Location
Houston
Occupation
Electrical Engineer
New member here with a question on Parallel Cable Runs

Let's say we have a 480VAC, 3-Phase, 15HP Motor, 550ft Cable Length, 75C Cable Rating, P.F. of 0.85, Copper Cable, and Temp Correction Factor of 1.
Using this information, and NEC430.250 I am seeing an FLA of 21[A].
Multiplying the FLA * 1.25 and using TableNEC240.6 I see a recommended upstream breaker size of 30A.
For Cable size based on Ampacity: Multiplying (UpstreamBreakerSize * TempCorrectionFactor) = (30A * 1) = 30 and using TableNEC310.16 i see a cable size of 10AWG
For Cable size based on 3%VoltageDrop: ( Sqrt(3) * 12.9 * CableLength * FLA) / CopperCM ) It appears 6AWG gives me 2.05%
Chosen cable size is the larger of the two above, so 6AWG.
Sorry for the long setup.

My question is a 2-parter:

1. Would having two parallel runs (same length and cable size per parallel run) change the formula for Cable Sizes as shown below?
New Cable Size Based on Ampacity: (UpstreamBreakerSize * TempCorrectionFactor) / NumberofParallelRuns and use TableNEC310.16 to get 14AWG per run
New Cable Size Based on 3%VD: ( Sqrt(3) * 12.9 * CableLength * FLA / NumberofParallelRuns) / CopperCM ) to get 10AWG at VD 2.59%

2. How would this affect upstream breaker size? Normally the cable needs to be sized to handle the full breaker ampacity. I would think that lowering the gauge of the cable would break this rule.
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
My question is a 2-parter:

1. Would having two parallel runs (same length and cable size per parallel run) change the formula for Cable Sizes as shown below?
New Cable Size Based on Ampacity: (UpstreamBreakerSize * TempCorrectionFactor) / NumberofParallelRuns and use TableNEC310.16 to get 14AWG per run
New Cable Size Based on 3%VD: ( Sqrt(3) * 12.9 * CableLength * FLA / NumberofParallelRuns) / CopperCM ) to get 10AWG at VD 2.59%
Yes...but parallel sets of #10awg are not allowed by the NEC.
2. How would this affect upstream breaker size? Normally the cable needs to be sized to handle the full breaker ampacity. I would think that lowering the gauge of the cable would break this rule.
It wouldn't. Two sets of #10 have an ampacity of 70. But for a motor the ampacity of the conductor does not need to match the breaker size.

If voltage drop was not a concern, the NEC would allow #10awg conductors on a 60A c/b for the 15hp, 460V motor that you described.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The conductors ares sized to 125% of the motor FLC from T430.250. The OCPD's for inverse time breakers can be up to 250% of the motor ampacity and is not based on the conductor size. Parallel conductors in general do not begin until the conductors are size #1/0 and larger.
 

TacoEngineer

Member
Location
Houston
Occupation
Electrical Engineer
The conductors ares sized to 125% of the motor FLC from T430.250. The OCPD's for inverse time breakers can be up to 250% of the motor ampacity and is not based on the conductor size. Parallel conductors in general do not begin until the conductors are size #1/0 and larger.
Understood on the parallel run size requirement, no issues there.
If we were to size the conductor based on 1.25% of FLC from NEC430.250, how would you size the upstream breaker? Could i use the same rule?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Understood on the parallel run size requirement, no issues there.
If we were to size the conductor based on 1.25% of FLC from NEC430.250, how would you size the upstream breaker? Could i use the same rule?
The OCPD needs to be large enough to allow the motor to start. 125% may or may not be larger enough. I'm unsure if engineers use a rule of thumb or there is some hard percentage that they use. Maybe someone will chime in. From the NEC's perspective you could use 250% of the motor current.
 

JoeStillman

Senior Member
Location
West Chester, PA
Understood on the parallel run size requirement, no issues there.
If we were to size the conductor based on 1.25% of FLC from NEC430.250, how would you size the upstream breaker? Could i use the same rule?
The breaker is not the overload protection for the motor branch-circuit cable. The starter overloads do that job. That is why the breaker is permitted (but not required) to be up to 250% of the FLA. It is required to be able to hold the starting current and 125% of FLA may not. YMMV.
 