Klockopotomis
- Parker CO
I am not understanding 310.12 NEC 2020 and the corresponding table.
If I understand it, you are allowed to derate up to 83 % the feeder or service conductors supplying a single or multi-family dwelling.
Example:
New overhead service for 200 amp main breaker panel fed from utility meter.
the supply side side conductors aka service entrance conductors can be derated according to 310.12 by 83%
If you look at Table 310.12 and follow 200 amp service or feeder rating it tells you 2/0 copper or 4/0 aluminum.
However, without derating, Table 310.16 lists 2/0 copper for 195 amps in the 90 deg column and 4/0 aluminum is listed for 205 amps.
So nothing changes...
I assumed if you could derate it then 83% or 200amps =166 Amps. which would be sized at 1/0 copper and 3/0 Aluminum
thoughts?
Example: