In our very large class last night I got a few questions wrong and to boil it down i think if i could understand the following I could understand why I got those questions wrong.
I have a 120/240 1 phase 3 wire panel and I run a multi wire branch circuit off breaker 1 and 3 and use a shared neutral with a 10 amp load on 1 and a 10 amp load on 3. So I've learned that if the neutral becomes open at the panel that my circuit becomes a series circuit and i am able to all the math on that senerio.
But, if I close the neutral on that circuit, i no longer have a series circuit? , even though the two loads are balanced and there are no amps flowing through the neutral.
So open neutral =no amps on the neutral, closed neutral= no amps on the neutral??
And what i really don't understand is if my closed neutral gives me a parallel circuit than why are my 10a and 10a not adding to 20 amps on breaker 1 and 20a on breaker 3??
Thanks for any help and the help in the past.
I have a 120/240 1 phase 3 wire panel and I run a multi wire branch circuit off breaker 1 and 3 and use a shared neutral with a 10 amp load on 1 and a 10 amp load on 3. So I've learned that if the neutral becomes open at the panel that my circuit becomes a series circuit and i am able to all the math on that senerio.
But, if I close the neutral on that circuit, i no longer have a series circuit? , even though the two loads are balanced and there are no amps flowing through the neutral.
So open neutral =no amps on the neutral, closed neutral= no amps on the neutral??
And what i really don't understand is if my closed neutral gives me a parallel circuit than why are my 10a and 10a not adding to 20 amps on breaker 1 and 20a on breaker 3??
Thanks for any help and the help in the past.