Assuming the max voltage drop allowed is 3% (not here to argue the 3% number) what happens if the source voltage is above or below the "standard" 120 volts.
115v - 3% = 111.5v
128v - 3% = 124.2v
If the source voltage is high, can there be a larger % of voltage drop? 128v at 10% voltage drop is 115.2v. which is more than adequate for any load
When plugging numbers into a voltage drop calculator, should you use 120v or the actual metered voltage?
I know that many loads can run on less than 115-120v, just looking to understand the theory behind the 3% number.
Thanks in advance
115v - 3% = 111.5v
128v - 3% = 124.2v
If the source voltage is high, can there be a larger % of voltage drop? 128v at 10% voltage drop is 115.2v. which is more than adequate for any load
When plugging numbers into a voltage drop calculator, should you use 120v or the actual metered voltage?
I know that many loads can run on less than 115-120v, just looking to understand the theory behind the 3% number.
Thanks in advance