understanding xformer
Toros
Tujunga, CA
hi
my client has a new industrial machine operating at 480v
and the available voltage-service in facility is 120/-240v, 4wire delta
Can I install an xformer: 480v-240v, 3-ph in reverse
(240v as primary and 480v as secondary)
or ,
I use an inverter
Thank you
xptpcrewx
Power System Engineer
Las Vegas, Nevada, USA
Licensed Electrical Engineer, Licensed Electrical Contractor, Certified Master Electrician
hi
or ,
I use an inverter
Thank you
You can get a transformer specifically made for reverse (step-up) operation.
GoldDigger
Placerville, CA, USA
Retired PV System Designer
Because of potential problems with the voltage ratio under load and with the inrush current when energized, not all transformers are recommended by their manufacturer for reverse usage. Check with the manufacturer of the transformer you want to use.
In the US the NEC now requires that the transformer be marked or described as OK for reverse operation before allowing such use.
jim dungar
Wisconsin
PE (Retired) - Power Systems
:thumbsup:
These units usually have 480Y/277 secondaries, so it is easy to solidly ground it instead of leaving it ungrounded or corner grounded, both of which have application issues.