Hi again,
I have a pentair pool panel that the pool guy ran a 1" sch. 40 pvc pipe from to the forming shell for the wet niche light. I planned on running a #8 THHN bonding wire to the forming shell and seal it with scotchkote. I believe I see 2 violations with this approach. (correct me if I'm wrong please and point out others)
1) The 1" PCV pipe needs to be sch. 80
2) A junction box with threaded conduit entries needs to be a min. of 4' away from the edge of the pool and 8 in. above the grade.
Or is the pentair pool panel listed for making the splice onto the GFI circuit?
I have a pentair pool panel that the pool guy ran a 1" sch. 40 pvc pipe from to the forming shell for the wet niche light. I planned on running a #8 THHN bonding wire to the forming shell and seal it with scotchkote. I believe I see 2 violations with this approach. (correct me if I'm wrong please and point out others)