2000a/208v existing switchgear, with 400mcm Cu x 6 per phase from the utility to a 2000a main breaker.
PV Output to be interconnected - 350a, 250mcm AL x 2 per phase from a service rated disconnect.
If accepted by the utility & AHJ, the desired interconnection would be supply-side.
My initial thoughts would be to either:
1.) Tap 2 of the supply conductors from each phase with the 250's from the PV. - Issue being 4 of the other supply phase conductors are untapped.
2.) Use a suitably rated terminal block to accommodate all conductors from supply and pv to complete the tap. - Is there a terminal block rated for that high an ampacity?
Any thoughts on the above or other suggested methods welcome.