uneven current

Status
Not open for further replies.

sparky59

Senior Member
I have a 2hp, 480 volt, three-phase, pump motor that has even voltage but the amps are 3.7,3.6, and 3.2 Is the motor going bad?
 
No it seems to be working fine. Is there a certain percentage difference in current draw that would signal that the motor is in trouble?
 
Sparky...

The Ampere-Imbalance-Factor (AIF) is about 9%. But, without knowing the corresponding Supply Voltage measurements one cannot say with assurance whether the problem is the supply or the motor!

If Supply voltage is the cause, then using the Rule-of-Thumb that Ampere-Imbalance is related to the square of Voltage-Imbalance, then the Voltage-Imbalance-Factor is 3%. The NEMA recommended maximum is 5%!

In conclusion,Yes, you may have a problem!

Regards, Phil
 
If the voltage is only slightly unbalanced it can create a much larger current unbalance.

A made a thread about a similar instance I had a couple years ago, but the search engine doesn't seem to be working right now so I can't link you to it.
 
Just FYI, if it is a submersible pump, the voltage balance factor is MUCH tighter than the NEMA standards, many are 2% and if you do not maintain it, you void the pump warranty (Franklin Pump is like that).
 