Unexplained Amperage

Status
Not open for further replies.

Sean_Carb

Member
I am currently working in Afghanistan doing construction jobs for the US Military. We just finished a project that included a small office building, 120/208V 400 A MDP, and 125 KVA generator set up. As we are going through our final inspection, the inspector decides to throw his amprobe on the equipment ground going from the MDP to the generator. He got a reading of 5.9A, needless to say he won't sign off the building until it is gone. So I began going through the system trying to find where this was coming from. The ground going between the subpanel inside the building and the MDP was reading 0 amps, all bonding wires and wires going to ground rods also read 0 amps. Only this one section of wire was coming back with a reading of any amperage. The nuetral and ground are bonded inside the alternator of the generator. And my system has an Ohm reading of less than 5 ohms, so I know the grounding system is sufficient. Now here is the kicker, remember how I said there is no amp reading on the ground wire from the subpanel inside the building to the MDP, only the ground from MDP to generator.......when you put your amprobe on that ground, and you turn off all the lights in the building.....it goes away completely. 0.0 amps! The building is using lithonia T-8 high efficiency electronic balast lights from the states! Can anyone shed some info on this???
 

brian john

Senior Member
Location
Leesburg, VA
1. Perform a zero sequence reading at the MDP
2. Do a zero sequence reading at the generator.
3. Turn off the light circuits one at a time, you most likely have a grounded neutral
at the MDP or in a branch circuit.
4. Turn off the system and turn off the CB's, isolate all the branch circuit neutrals and the
feeder to the generator, megger all of these conductors and locate the "short".
5. Check the neutral bus in the MDP for a ground connection
 

Sean_Carb

Member
When our company installs a generator, the PM from our generator division always has his guys bond neutral and ground in the alternator. I checked myself and it is there. Also, I supervised the installation of the MDP so i know there isn't one there.
 

brian john

Senior Member
Location
Leesburg, VA
When our company installs a generator, the PM from our generator division always has his guys bond neutral and ground in the alternator. I checked myself and it is there. Also, I supervised the installation of the MDP so i know there isn't one there.

Ahhhhhh, but did you test it? and all down stream neutrals.
 

brian john

Senior Member
Location
Leesburg, VA
I have asked this before (see previous post) but what was the issue.

I like to know what was wrong and how this was resolved. I think this forum deserves that much from posters asking questions and getting several avenues to check.

If we are wrong shouldn't we be told the solution to add to our knowledge base.

I know many posters may be real busy and getting back to post may be a PIA, but heck it only takes a few minutes to say the answer to my problem was XXXXXXXXXXXXXXX.
 

ceb58

Senior Member
Location
Raeford, NC
I have asked this before (see previous post) but what was the issue.

I like to know what was wrong and how this was resolved. I think this forum deserves that much from posters asking questions and getting several avenues to check.

If we are wrong shouldn't we be told the solution to add to our knowledge base.

I know many posters may be real busy and getting back to post may be a PIA, but heck it only takes a few minutes to say the answer to my problem was XXXXXXXXXXXXXXX.

Well said, Brian
 

Smart $

Esteemed Member
Location
Ohio
...

I know many posters may be real busy and getting back to post may be a PIA, but heck it only takes a few minutes to say the answer to my problem was XXXXXXXXXXXXXXX.
With problems such as this, I usually attribute the solution to one which the poster adamantly stated, swore, or otherwise asserted as not being the problem :roll:
 