My client is a large international bank. For the past year, they have experienced strange and unexplained occurrences with their power distribution boards (sub-boards) in their office.
Let me describe a brief architecture arrangement of the distribution system in question. In the office, power supply to desks, sockets and other equipment is distributed by various sub-boards. The sub-boards are 3 phase panel but are normally wired for 10 to 16 single phase outgoing circuits. There is a main isolator (not a circuit breaker) in each of the sub-board.
Upstream of each sub-board, a circuit breaker of an appropriated rating is installed in a main distribution panel (main-boards) to protect the down-stream sub-board.
What happened for the past year?
There were over 10 incidences occurred over 6 months? period where different sub-boards with no ?out-going? circuits experienced internal flashover or arcing. There are no loads connected to the sub-boards.
The flashover occurs where the 20A single phase circuit breakers plugged into the main bus bar of the sub-board. The bus bar of the particular bland of sub-boards is made of male type of connectors. The female type sockets circuit breakers plugged into the bus bar and it is at the point of connections were the flashover or arcing occurred. There are damages at the point of connections especially at the tip of made plugs of the sub-boards bus bar. A small flashover burnt mark is also left on the surface of the circuit breaker.
When this occurred, the 20A circuit breaker did not trip. The tripping occurred at the upstream main-board circuit breaker feeding the sub-board.
Full investigations were conducted on the affected sub-boards for workmanship which included lab tests and insulation tests. No apparent defeats were found and the problem remains unresolved.
What happen inside the sub-boards and why are there flashovers when there are no loads connected? Please help out.
Let me describe a brief architecture arrangement of the distribution system in question. In the office, power supply to desks, sockets and other equipment is distributed by various sub-boards. The sub-boards are 3 phase panel but are normally wired for 10 to 16 single phase outgoing circuits. There is a main isolator (not a circuit breaker) in each of the sub-board.
Upstream of each sub-board, a circuit breaker of an appropriated rating is installed in a main distribution panel (main-boards) to protect the down-stream sub-board.
What happened for the past year?
There were over 10 incidences occurred over 6 months? period where different sub-boards with no ?out-going? circuits experienced internal flashover or arcing. There are no loads connected to the sub-boards.
The flashover occurs where the 20A single phase circuit breakers plugged into the main bus bar of the sub-board. The bus bar of the particular bland of sub-boards is made of male type of connectors. The female type sockets circuit breakers plugged into the bus bar and it is at the point of connections were the flashover or arcing occurred. There are damages at the point of connections especially at the tip of made plugs of the sub-boards bus bar. A small flashover burnt mark is also left on the surface of the circuit breaker.
When this occurred, the 20A circuit breaker did not trip. The tripping occurred at the upstream main-board circuit breaker feeding the sub-board.
Full investigations were conducted on the affected sub-boards for workmanship which included lab tests and insulation tests. No apparent defeats were found and the problem remains unresolved.
What happen inside the sub-boards and why are there flashovers when there are no loads connected? Please help out.