We re-worked some power to a remote location roughly around 1500 feet long run. It’s was 240v direct buried 2awg aluminum.
But there is now some added load at the end so a 600v 120/240v transformer was added to step up right after the service than step back down at the location.
I know it’s not a proper step up transformer rather than back feeding it which is where the problem arises.
The 600volt conductors are ungrounded and have no detection system. Rather than proposing a ground detection system I am going to go with either grounding the center tap of the primary winding (600v) .
Can anyone see a problem with this?
It’s a 10kva tranny. Primary protection before the transformer is at the service on the 240volt side.
Conductors go straight to the other transformer nothing in between. No disco or ocpd inbetween. Is any needed for the 2nd tranny? I know we can label where the lockable disconnection means is. But can the same disconnect work for both transformers.
Another problem I see is once the conductors are stepped back down to 120/240v they terminate directly into a main lug only panel. I was under the assumption they must terminate into a single breaker or fuses. Or can the breakers not just add up to the allowed sum of the single breaker?
Below is the tranny nameplate.

But there is now some added load at the end so a 600v 120/240v transformer was added to step up right after the service than step back down at the location.
I know it’s not a proper step up transformer rather than back feeding it which is where the problem arises.
The 600volt conductors are ungrounded and have no detection system. Rather than proposing a ground detection system I am going to go with either grounding the center tap of the primary winding (600v) .
Can anyone see a problem with this?
It’s a 10kva tranny. Primary protection before the transformer is at the service on the 240volt side.
Conductors go straight to the other transformer nothing in between. No disco or ocpd inbetween. Is any needed for the 2nd tranny? I know we can label where the lockable disconnection means is. But can the same disconnect work for both transformers.
Another problem I see is once the conductors are stepped back down to 120/240v they terminate directly into a main lug only panel. I was under the assumption they must terminate into a single breaker or fuses. Or can the breakers not just add up to the allowed sum of the single breaker?
Below is the tranny nameplate.