Guys can anyone tell me if its mandatory to identify all ungrounded conductors if the voltge is nominal 208/120. Ex. 3 # 10s and grnd to a 30 amp 3 phase disconnect do they have to be taped blue,black, red?
Not sure about the colors, but IMO they do need to be identified
Looks like 210.5(C)1,2,3 answers this