I have searched pretty hard for this scenario and haven't had any luck, hopefully you guys can help.
I work at an industrial plant with 480V three phase ungrounded deltas for most MCCs. The MCCs all have ground fault indicating lights and the other day we had B Phase light go out in MCC #1 and MCC #2, Phase A and C lights lit brighter, as they were obviously getting higher voltage due to the ground fault. We began shutting off buckets until we got to a 480V to 240V transformer, which corrected the ground fault. This transformer then feeds a main breaker panel, which then feeds a sub panel. On this sub panel circuit #13 is a 2 pole 240V breaker for a blower fan for an air conditioner (not the condenser). Upon turning this breaker off, the ground fault disappeared. We disconnected the fan motor and turned the breaker back on, and everything went back to normal.
So as most of you know, the reason the ground fault lights act as they do is that when a ground fault occurs you are now reading 480V (in this case) on A and C phase to ground (which is now essentially B Phase), and 0V on B, as there is no longer any potential. In this particular case though, there isn't 480V going to ground, there is only 120V going to ground. In theory I would assume the breaker should have tripped, but there's a chance it's oversized (somewhat beside the point). So the question is, how and why did this happen? We don't technically have a 480V short to ground, so why are the lights acting as if we do (voltage across A phase light and C phase light was 480V)? I've talked this over with a few coworkers and no one has had a solid concrete answer other than "PFM". Some people speculate there is some sort of back feeding, but they don't really know, or can't explain it.
Thanks in advance!
I work at an industrial plant with 480V three phase ungrounded deltas for most MCCs. The MCCs all have ground fault indicating lights and the other day we had B Phase light go out in MCC #1 and MCC #2, Phase A and C lights lit brighter, as they were obviously getting higher voltage due to the ground fault. We began shutting off buckets until we got to a 480V to 240V transformer, which corrected the ground fault. This transformer then feeds a main breaker panel, which then feeds a sub panel. On this sub panel circuit #13 is a 2 pole 240V breaker for a blower fan for an air conditioner (not the condenser). Upon turning this breaker off, the ground fault disappeared. We disconnected the fan motor and turned the breaker back on, and everything went back to normal.
So as most of you know, the reason the ground fault lights act as they do is that when a ground fault occurs you are now reading 480V (in this case) on A and C phase to ground (which is now essentially B Phase), and 0V on B, as there is no longer any potential. In this particular case though, there isn't 480V going to ground, there is only 120V going to ground. In theory I would assume the breaker should have tripped, but there's a chance it's oversized (somewhat beside the point). So the question is, how and why did this happen? We don't technically have a 480V short to ground, so why are the lights acting as if we do (voltage across A phase light and C phase light was 480V)? I've talked this over with a few coworkers and no one has had a solid concrete answer other than "PFM". Some people speculate there is some sort of back feeding, but they don't really know, or can't explain it.
Thanks in advance!