A buddy of mine asked me to look at a $10,000+ complete rewire of his grandson's old house.
I started out looking at the wiring in the gazebo because that was the first thing on the path from the car to the house. I found a conduit coming up from the ground into a metal cast box with a grounding screw and a GFCI, a gland fitting with NM coming out of the top of the box to another metal box containing the light switch. From that box cable continued up to another box containing
another GFCI under the roof which also had a cable going to a lighting fixture. The lighting fixture was a new LED device.
There was one piece of UF, with the rest NM.
Here are the problems I found:
0) Unable to determine if wire in conduit was rated for wet locations
1) Use of NM-B cable in a damp location (Gazebo poles and under roof).
100 Location, Damp
100 Location, Wet
334.10(A) describes NM -- no mention of damp/wet but 334.10(B) NMC mentions damp/wet -- hence NM can not be used in damp/wet locations
2) Use of GFCI outdoors that is not listed/marked as WR.
406.4(D)(6)
406.9(A) and (B)
3) Ground wires twisted together without using a listed connector
110.14(B)
4) Metal box ungrounded
-- using a Low-Z DVM I read 123VAC hot--neutral; 123VAC hot--ground wire; 0.063VAC hot--ground screw on box
250.96(A)
5) GFCI used to feed 24 hour circuit plugged into it without an in-use cover.
406.9(B)(2)(a)
6) GFCI not-in-use cover mounted sideways, opening left to right, not up to down
110.3(B)
Interested in an evaluation of these results. [2011 is current adopted code -- no amendments]
This was just the tip of the iceberg.
I started out looking at the wiring in the gazebo because that was the first thing on the path from the car to the house. I found a conduit coming up from the ground into a metal cast box with a grounding screw and a GFCI, a gland fitting with NM coming out of the top of the box to another metal box containing the light switch. From that box cable continued up to another box containing
another GFCI under the roof which also had a cable going to a lighting fixture. The lighting fixture was a new LED device.
There was one piece of UF, with the rest NM.
Here are the problems I found:
0) Unable to determine if wire in conduit was rated for wet locations
1) Use of NM-B cable in a damp location (Gazebo poles and under roof).
100 Location, Damp
100 Location, Wet
334.10(A) describes NM -- no mention of damp/wet but 334.10(B) NMC mentions damp/wet -- hence NM can not be used in damp/wet locations
2) Use of GFCI outdoors that is not listed/marked as WR.
406.4(D)(6)
406.9(A) and (B)
3) Ground wires twisted together without using a listed connector
110.14(B)
4) Metal box ungrounded
-- using a Low-Z DVM I read 123VAC hot--neutral; 123VAC hot--ground wire; 0.063VAC hot--ground screw on box
250.96(A)
5) GFCI used to feed 24 hour circuit plugged into it without an in-use cover.
406.9(B)(2)(a)
6) GFCI not-in-use cover mounted sideways, opening left to right, not up to down
110.3(B)
Interested in an evaluation of these results. [2011 is current adopted code -- no amendments]
This was just the tip of the iceberg.